F01681 fault in siemens S120 Drive

1 Posts
1 Users
0 Reactions
314 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : SI Motion P1- Incorrect parameter value comes when the actual checksum calculated by the drive and entered in r9728 via the safety-relevant parameters does not match the reference checksum saved in p9729 at the last machine acceptance.

Safety-relevant parameters have been changed or a fault is present.

Fault value (r0949, interpret decimal):

0: Checksum error for SI parameters for motion monitoring.
1: Checksum error for SI parameters for actual values.
2: Checksum error for SI parameters for component assignment.

- check the safety-relevant parameters and if required, correct.
- execute the function "Copy RAM to ROM".
- perform a POWER ON if safety parameters requiring a POWER ON have been modified.
- carry out an acceptance test.