Cause : Safely limited position limit values interchanged comes when the function "Safely Limited Position" (SLP), a lower value is in p9534 than in p9535.
Fault value (r0949, interpret decimal):
1: Limit values SLP1 interchanged.
2: Limit values SLP2 interchanged.
See also: p9534, p9535
- correct the lower and upper limit values (p9535, p9534).
- carry out a POWER ON (power off/on).