Siemens SINAMICS S120/S150 Drive
1
Posts
1
Users
0
Reactions
151
Views
Feb 21, 2024 5:52 am
Cause : Synchronization unsuccessful comes when synchronization between the basic clock cycle, DRIVE-CLiQ clock cycle and application clock cycle was started and was not able to be successfully completed (e.g. after switch-on).
1. Remove the cause of a possible DRIVE-CLiQ fault.
2. Initiate a new synchronization, e.g. as follows:
- remove the PROFIBUS master and re-insert again.
- restart the PROFIBUS master.
- switch-off the Control Unit and switch-on again.
- carry out a Control Unit hardware reset (RESET button, p0972).
- carry out a parameter reset and download the saved parameters (p0009 = 30, p0976 = 2, 3)