F03001 fault in siemens S120 Drive

1 Posts
1 Users
0 Reactions
129 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : NVRAM checksum incorrect comes when a checksum error occurred when evaluating the non-volatile data (NVRAM) on the Control Unit. The NVRAM data affected was deleted.

Carry out a POWER ON (power off/on) for all components.