Forum

Share:
Notifications
Clear all

F05065 fault in siemens S120 Drive

1 Posts
1 Users
0 Reactions
190 Views
Posts: 18126
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Voltage measured values not plausible comes when the voltage measurement does not supply any plausible values and is not used.

Alarm value (r2124, interpret bitwise binary):

Bit 1: Phase U
Bit 2: Phase V
Bit 3: Phase W

The following parameterization must be made in order to deactivate the alarm:

- Deactivate voltage measurement (p0247.0 = 0).
- Deactivate flying restart with voltage measurement (p0247.5 = 0) and deactivate fast flying restart (p1780.11 = 0)

Share: