Cause : Voltage measured values not plausible comes when the voltage measurement does not supply any plausible values and is not used.
Alarm value (r2124, interpret bitwise binary):
Bit 1: Phase U
Bit 2: Phase V
Bit 3: Phase W
The following parameterization must be made in order to deactivate the alarm:
- Deactivate voltage measurement (p0247.0 = 0).