Siemens SINAMICS S120/S150 Drive
1
Posts
1
Users
0
Reactions
217
Views
Feb 21, 2024 9:19 am
Cause : Bypass contactor simultaneity monitoring time exceeded comes when a feedback signal for the bypass contactor is interconnected and the simultaneity monitoring (p0255[5, 7]) activated.
After opening or closing a contactor of the parallel connection, after a monitoring time has elapsed, not all of the contactors have assumed the same state.
- check the monitoring time setting (p0255[5, 7]).
- check the wiring and control of the contactor.
- if required, replace the contactor.