F06010 fault in siemens S120 Drive

1 Posts
1 Users
0 Reactions
872 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Power unit EP 24 V missing in operation comes when the pulse enable via terminal EP at the Line Module (X21.3, X21.4) was withdrawn.

- do not open the line side switch in operation - only when the pulses are inhibited.
- check the wiring of terminal EP (X21.3, X21.4) at the Line Module to exclude any poor contacts