Cause : Temperature threshold value outside the measuring range comes when the fault number specifies the number of the VSM where the fault occurred:
0: For sensor type KTY p3665=2, p3667/p3668 is outside the value range from 181°C up to 300°C .
1: For sensor type KTY p5465[0]=2, p5467[0]/p3668[0] is outside the value range from 181°C up to 300°C .
2: For sensor type KTY p5465[1]=2, p5467[1]/p3668[1] is outside the value range from 181°C up to 300°C .
Depending on the fault value (number of the VSM), the following applies:
0: For sensor type KTY p3665=2, p3667/p3668 should be set within the value range from 181°C up to 300°C .
1: For sensor type KTY p5465[0]=2, p5467[0]/p5468[0] should be set within the value range from 181°C up to 300°C .
2: For sensor type KTY p5465[1]=2, p5467[1]/p5468[1] should be set within the value range from 181°C up to 300°C .
See also: p0221, p3660, p3670, p3676