Cause : Project conversion error comes when converting the project of an older firmware version, an error occurred.
Parameter number of the parameter causing the error.
For fault value = 600, the following applies:
- The temperature evaluation is no longer assigned to the power unit but to the encoder evaluation.
- Check the parameter indicated in the fault value and correctly adjust it accordingly.
For fault value = 600:
Parameter p0600 must be set to the values 1, 2 or 3 in accordance with the assignment of the internal encoder evaluation to the encoder interface.
- Value 1 means: The internal encoder evaluation is assigned to the encoder interface 1 via p0187.
- Value 2 means: The internal encoder evaluation is assigned to the encoder interface 2 via p0188.
- Value 3 means: The internal encoder evaluation is assigned to the encoder interface 3 via p0189.
- If necessary, the internal encoder evaluation must be assigned to an encoder interface via parameters p0187, p0188 or p0189 accordingly.
- If necessary, upgrade the firmware to a later version.