N01507 in siemens S120 Drive

1 Posts
1 Users
0 Reactions
270 Views
Posts: 18456
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Interconnections to inactive objects present comes when there are BICO interconnections to an inactive/inoperable drive object.

  1. The BI/CI parameters involved are listed in r9498.
  2. The associated BO/CO parameters are listed in r9499.
  3. The list of the BICO interconnections to other drive objects is displayed in r9491 and r9492 of the de-activated drive object.

- set all open BICO interconnections centrally to the factory setting with p9495 = 2.
- make the non-operational drive object active/operational again (re-insert or activate components).