Cause : motor holding brake/SBC configuration not practical comes when a configuration of motor holding brake and SBC was detected that is not practical. The following configurations can result in this message:
- "No motor holding brake available" (p1215 = 0) and "SBC" enabled (p9602 = 1).
- "Motor holding brake just like the sequence control, connection via BICO" (p1215 = 3) and "SBC" enabled (p9602 = 1).
- Check the parameterization of the motor holding brake and SBC and correct.
- See also: p1215 (Motor holding brake configuration), p9602 (SI enable Safe Brake Control (Control Unit)), p9802 (SI enable Safe Brake Control (Motor Module)).