Cause : Vdc_max controller active comes when the Vdc_max controller works to keep the DC-link voltage (r0026) below the level specified in r1242.
Check the following:
• Supply voltage must lie within limits indicated on rating plate.
• Ramp-down time (P1121) must match inertia of load.
Note: Higher inertia requires longer ramp times; other- wise, apply braking resistor.