F64 fault in siemens V20 Drive

1 Posts
1 Users
0 Reactions
230 Views
Posts: 18069
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Inverter attempted to do an automatic clone during startup comes when no Clone00.bin file in the correct directory /USER/SINAMICS/DATA.

If an automatic clone is required then follow these steps:

  • Insert the MMC/SD card with correct file and power-cycle. If no automatic clone is required:
  • Remove the card if not needed and power- cycle.
  • Reset P8458 = 0 and power-cycle.

Note: Fault can only be cleared by a power-cycle.