This document will describe how to setup the PSTX on EtherNet/IP and interface with a Rockwell PLC with Studio 5000 software.

The PSTX first needs to be programmed for EtherNet/IP:

  • 12.02 FB interface connector = Anybus
  • 12.03 Fieldbus control; = On (for control via EtherNet/IP)
  • 12.05 IP address = IP address of the PSTX
  • 12.06 Gateway = Gateway address if used
  • 12.07 Subnet Mask = Subnet Mask
  • 12.08 DHCP = OFF
  • 12.11-12.21 =Settings for different status bits to monitor
  • 12.22-12.31 Fieldbus AI =Programmable to monitor values over fieldbus.

The PLC needs to be setup with the Generic module with assemblies:

  • 100 size 12 words in
  • 150 size 5 words out

Below is the Status word and data to be received back from the PSTX.

Below image show status word and additional programmable bits with parameters 12.11-12.21

Below image show additional input words programmable via parameters 12.22-12.31

Below image shows the Control word: