Softstarter
1
Posts
1
Users
0
Reactions
363
Views
Jun 24, 2024 12:29 pm
This document will describe how to setup the PSTX on EtherNet/IP and interface with a Rockwell PLC with Studio 5000 software.
The PSTX first needs to be programmed for EtherNet/IP:
- 12.02 FB interface connector = Anybus
- 12.03 Fieldbus control; = On (for control via EtherNet/IP)
- 12.05 IP address = IP address of the PSTX
- 12.06 Gateway = Gateway address if used
- 12.07 Subnet Mask = Subnet Mask
- 12.08 DHCP = OFF
- 12.11-12.21 =Settings for different status bits to monitor
- 12.22-12.31 Fieldbus AI =Programmable to monitor values over fieldbus.
The PLC needs to be setup with the Generic module with assemblies:
- 100 size 12 words in
- 150 size 5 words out
Below is the Status word and data to be received back from the PSTX.
Below image show status word and additional programmable bits with parameters 12.11-12.21
Below image show additional input words programmable via parameters 12.22-12.31
Below image shows the Control word: