How can resolve problem Lvd fault in delta VFD-ED series drive ?
1 Reply
DC bus voltage during deceleration is less than the setting in Pr.06-00.
corrective action
1. Check if the input voltage is normal.
2. Check for possible sudden load change.
Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.