Delta VFD-ED Series Drive
2
Posts
1
Users
0
Reactions
374
Views
Jun 04, 2022 10:57 am
How can resolve problem ocd fault in delta VFD-ED series drive ?
1 Reply
Jun 04, 2022 10:59 am
Over-current during deceleration (output current exceeds three times the drive’s rated current during deceleration).
corrective action
1. Short-circuit at motor output: Check for possible poor insulation at the output.
2. Deceleration Time is too short: Increase the Deceleration Time.
3. AC motor drive output power is too small: Replace the AC motor drive with a higher power model.