Forum

Share:
Notifications
Clear all

ocn fault in delta VFD-ED series drive

2 Posts
1 Users
0 Reactions
217 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem ocn fault in delta VFD-ED series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over-current during steady operation (output current exceeds three times the drive’s rated current during constant speed).

corrective action

1. Short-circuit at motor output: Check for possible poor insulation at the output.

2. Sudden increase in motor load: Check for possible motor stall.

3. AC motor drive output power is too small: Replace the AC motor drive with a higher power model.

ocn delta ed

Reply
Share: