How can resolve problem oH1 fault in delta VFD-ED series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

IGBT overheating : IGBT temperature exceeds protection level

corrective action

1. Ensure that the ambient temperature falls in the specified temperature range.

2. Make sure heat sink is not obstructed. Check if the fan i operating.

3. Check if there is enough ventilation clearance for the AC motor drive.

Reply