ovd fault in delta VFD-ED series drive

2 Posts
1 Users
0 Reactions
441 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem ovd fault in delta VFD-ED series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

DC bus over-voltage during deceleration

230V: 405 VDC ; 460V: 810 VDC

corrective action

1. Check if the input voltage falls in the rated AC motor drive input voltage range.

2. Check for possible voltage transients.

3. If DC bus over-voltage due to regenerative voltage, increase the Deceleration Time or add an optional brake resistor.

Reply