How can resolve problem ovS fault in delta VFD-ED series drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Over-voltage at stop
Hardware failure in voltage detection.
corrective action
1. Check if the input voltage falls in the rated AC motor drive input voltage range.
2. Check for possible voltage transients.
Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.