Forum

Share:
Notifications
Clear all

STO fault in delta VFD-ED series drive

2 Posts
1 Users
0 Reactions
913 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem STO fault in delta VFD-ED series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

STO Safe Torque Off - Safe Torque Off function is enabled.

corrective action

1. Check the wiring for STO1/SCM1 and STO2/SCM2.
2. Reset the emergency switch (ON) and reboot the motor drive.
3. Check the voltage at least > 11 V.
4. Check the wiring between STO1/STO2 and E24V, and the wiring between SCM1/SCM2 and DCM.
5. After checking all the wiring, reboot the motor drive.

 

Reply