Cause : Ground fault comes when there is current from the output phases to ground, either in the cable between the adjustable frequency drive and the motor or in the motor itself.
Troubleshooting :
- Remove power to the adjustable frequency drive and repair the ground fault.
- Check for ground faults in the motor by measuring the resistance to ground of the motor leads and the motor with a megohmmeter.