Cause : External fan fault comes when the fan warning function is an extra protective function that checks if the fan is running/mounted. The fan warning can be disabled in 14-53 Fan Monitor ([0] Disabled).
Troubleshooting :
- Check for proper fan operation.
- Cycle power to the adjustable frequency drive and check that the fan operates briefly at start- up.
- Check the sensors on the heatsink and control card.