WARNING/ALARM 17 in VLT FC102 drive

1 Posts
1 Users
0 Reactions
210 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Control word timeout comes when there is no communication to the adjustable frequency drive. The warning is only active when 8-04 Control Word Timeout Function is NOT set to [0] Off.

If 8-04 Control Word Timeout Function is set to [5] Stop and Trip, a warning appears and the adjustable frequency drive ramps down until it stops then displays an alarm.

Troubleshooting :

  • Check connections on the serial communication cable.
  • Increase 8-03 Control Word Timeout Time.
  • Check the operation of the communication equipment.
  • Verify a proper installation based on EMC requirements.