ALARM 29 in VLT FC103 Drive
Cause : Heat Sink temp comes when the maximum temperature of the heat sink has been exceeded. The temperature fault does not reset until the temperature drops below a defined heat sink temperature.
The trip and reset points are different based on the frequency converter power size.
  • Check for the following conditions
  • Ambient temperature too high
  • Motor cable too long
  • Incorrect airflow clearance above and below the frequency converter
  • Blocked airflow around the frequency converter
  • Damaged heat sink fan
  • Dirty heat sink : This alarm is based on the temperature measured by the heat sink sensor mounted inside the IGBT modules.
  • Check fan resistance.
  • Check soft charge fuses.
  • Check IGBT thermal sensor.