Forum

Share:
Notifications
Clear all

WARNING 59 in danfoss VLT FC103 Drive

1 Posts
1 Users
0 Reactions
280 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Current limit comes when the current is higher than the value in 4-18 Current Limit. "Current limit" typically refers to a feature found in electronic devices, such as power supplies, motor controllers, or Variable Frequency Drives (VFDs).

This feature allows users to set a maximum limit on the amount of current that can flow through the device or system.

  1. Ensure that motor data in parameters 1-20 to 1-25 are set correctly.
  2. Possibly increase the current limit.
  3. Be sure that the system can operate safely at a higher limit.
Share: