WARNING/ALARM 104 in danfoss VLT FC103 Drive

1 Posts
1 Users
0 Reactions
108 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Mixing fan fault comes when fan monitor checks that the fan is spinning at frequency converter power-up or whenever the mixing fan is turned on.

  1. If the fan is not operating, then the fault is annunciated.
  2. The mixing-fan fault can be configured as a warning or an alarm trip by 14-53 Fan Monitor.
  3. Cycle power to the frequency converter to determine if the warning/alarm returns.