AEr alarm code in yaskawa V1000 drive

1 Posts
1 Users
0 Reactions
168 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Station Address Setting Error (CC-Link, CANopen, MECHATROLINK) comes when option card node address is outside of the acceptable setting range. Station number is set outside the possible setting range.

• Set parameter F6-10 to the proper value when using a CC-Link option.
• Set parameter F6-35 to the proper value when using a CANopen option.