426
Mar 21, 2024 4:49 pm
Cause : Power Supply Undervoltage comes when the input power supply voltage became equal to or lower than the Input Power Supply Undervoltage Detection Level (L2-21).
200 V Class: Approximately 150 Vrms
400 V Class: Approximately 300 Vrms
- The capacity of the power supply is too small.
- Increase the capacity of the power supply.
- The distortion in the power supply is too large.
- Lower the impedance of the input power supply wiring.
- A phase loss occurred in the input power supply.
- Check the input power supply for phase loss or an imbalance in the interphase voltages.
- Investigate and correct the cause and then reset the fault.
