Cause : Braking Transistor Overload Fault comes when the braking transistor in the drive has been overloaded.
- The proper braking resistor has not been installed. Select the proper braking resistor.
- Use a regen converter, regen unit, braking unit, or other device to connect the +1 or +3 terminal to the - terminal. Set L8-55 to 0 to disable Internal Braking Transistor Protection.
- The use rate of the braking transistor is high (i.e., the regen converter is large or the repetition frequency is high).
• Change to a CDBR type braking unit.
• Change to a regen converter.
• Increase the deceleration time. - The braking transistor inside the drive is faulty. Replace the drive.