Cause : Polarity Judge Timeout comes when disconnection in the motor coil winding or loose output terminals.
• Measure the motor line-to-line resistance and replace the motor if the motor coil winding is open.
• Check for loose terminals. Apply the tightening torque specified in this manual to fasten the terminals