EF2 alarm code in yaskawa A1000 drive
Cause : External Fault (Input Terminal S2) comes when external fault at multi-function input terminal S2. An external device has tripped an alarm function.
  1. Remove the cause of the external fault and reset the multi-function input value.
  2. Wiring is incorrect.
    • Ensure the signal lines have been connected properly to the terminals assigned for external fault detection (H1-.... = 2C to 2F).
    • Reconnect the signal line
  3. Multi-function contact inputs are set incorrectly.
    • Check if the unused terminals have been set for H1-.... = 2C to 2F (External Fault).
    • Change the terminal settings.