Yaskawa A1000, U1000, V1000 & V1000-4X Drive
1
Posts
1
Users
0
Reactions
197
Views
Mar 22, 2024 12:11 pm
Cause : External Fault (Input Terminal S4) comes when external fault at multi-function input terminal S4. An external device has tripped an alarm function.
- Remove the cause of the external fault and reset the multi-function input value.
- Wiring is incorrect.
• Ensure the signal lines have been connected properly to the terminals assigned for external fault detection (H1-.... = 20 to 2F).
• Reconnect the signal line - Multi-function contact inputs are set incorrectly.
• Check if the unused terminals have been set for H1-XX = 20 to 2F (External Fault).
• Change the terminal settings.