Yaskawa A1000, U1000, V1000 & V1000-4X Drive
1
Posts
1
Users
0
Reactions
451
Views
Mar 17, 2024 5:13 pm
Cause : Motor Data Error comes when motor data or data entered during Auto-Tuning was incorrect or motor rated power and motor-rated current settings (T1-02 and T1-04) do not match.
- Check that the motor data entered to T1 parameters matches motor nameplate input before Auto-Tuning.
- Restart Auto-Tuning and enter the correct information.
- Check the drive and motor capacities.
- Correct the settings of parameters T1-02 and T1-04.
- Motor rated current and detected no-load current are inconsistent.
- Check the motor rated current and no-load current.
- Correct the settings of parameters T1-04 and E2-03.
- Base frequency and motor rated speed (T1-05 and T1-07) do not match.
- Correct the settings of parameters T1-05 and T1-07.
- Check that the correct number of poles were entered to T1-06.