Forum
Share:
Notifications
Clear all
Er-09 alarm code in yaskawa U1000 drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
Cause : Acceleration Error comes when the motor did not accelerate for the specified acceleration time or torque limit when motoring is too low (L7-01 and L7-02).
  1. The load was too high during Rotational Auto-Tuning.
  2. Increase the acceleration time (C1-01).
  3. Disconnect the machine from the motor if possible.
  4. Check L7-01 and L7-02 settings.
  5. Increase the setting.
  6. Disconnect the motor from machine and restart Auto-Tuning. If motor and load cannot be uncoupled make sure the load is lower than 30%.
  7. If a mechanical brake is installed, make sure it is fully lifted during tuning.