427
Mar 17, 2024 5:52 pm
Cause : Z Pulse Correction Error comes when motor was coasting when Auto-Tuning was performed or either the motor or the PG encoder on the motor are not properly wired.
- The direction for the PG encoder is set incorrectly, or the number of pulses set for the PG encoder is wrong.
- Make sure the motor comes to a complete stop. Repeat Auto-Tuning.
- Check the wiring for the motor and the PG encoder. Restart Auto-Tuning.
- Check the direction and number of pulses set for the PG encoder. Restart Auto-Tuning.
- PG encoder is damaged.
- Check the signal output from the PG encoder attached to the motor. Replace the PG if damaged.
- Motor inertia is large.
- Increase the setting of n8-02 (Pole Attraction Current).
- Z-Pulse Offset Tuning was performed when b1-04 was set to 1.
• Z-Pulse Offset Tuning cannot be performed for a machine with reverse operation prohibited.
• If the machine allows reverse operation, set b1-04 to 0 to enable Reverse Operation Selection and then perform Z-Pulse Offset Tuning. - Motor vibrates during tuning. • Increase the setting of n8-03, Current Startup Time, and n8-04, Pole Attraction Time.
• Decrease the setting of n8-02, Pole Attraction Current.