Cause : Internal Fan Fault comes when an or magnetic contactor failure (detected when L8-32 = 0 to 2) or internal cooling fan has malfunctioned.
- Fault detected in the internal cooling fan or magnetic contactor to the power supply.
- Cycle power to the drive.
- Check for fan operation.
- Verify the cumulative operation time of the fan with monitor U4-03, and verify the cumulative operation time of the fan maintenance timer with U4-04.
- If the cooling fan has exceeded its expected performance life or is damaged in any other way, replace the fan.
• Cycle power to the drive.
• If the fault continues to occur, replace the power board/gate drive board or the entire drive.