FbH fault code in yaskawa V1000 drive

1 Posts
1 Users
0 Reactions
195 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Excessive PID Feedback comes when PID feedback input is greater than the level set to b5-36 for longer than the time set to b5-37. Set b5-12 to 2 or 5 to enable fault detection.

  1. Parameters are set inappropriately- check b5-36 and b5-37 settings.
  2. Incorrect PID feedback wiring- correct the wiring.
  3. There is a problem with the feedback sensor- check the sensor on the control side or replace the sensor if damaged.