Cause : PID Feedback Loss comes when the PID feedback input is lower than the level set to b5-13 for longer than the time set to b5-14.
- Parameter settings for b5-13 and b5-14 are incorrect. Check parameters b5-13 and b5-14.
- PID feedback wiring is faulty. Correct the wiring.
- Feedback sensor has malfunctioned. Check the sensor and replace it if damaged.
- Feedback input circuit is damaged. Replace either the control board or the entire drive.