FbL fault code in yaskawa V1000 drive
Cause : PID Feedback Loss comes when PID feedback loss detection is programmed to trigger a fault (b5-12 = 2 or 5) and the PID feedback level is below the detection level set to b5-13 for longer than the time set to b5-14.
  1. Parameters are set inappropriately Check b5-13 and b5-14 settings.
  2. Incorrect PID feedback wiring Correct the wiring.
  3. There is a problem with the feedback sensor- check the sensor on the control side or replace the sensor if damaged.