Cause : LSo Fault comes when pull-out has been detected at low speed due to the incorrect motor code has been entered or the load is too heavy.
- The drive incorrectly detected the position of the motor poles.
- Values set to parameters L8-93, L8-94, and L8-95 are incorrect.
- Enter the correct motor code for the PM motor being used into E5-01.
- For special-purpose motors, enter the correct data to all E5 parameters according to the test report provided for the motor.
- Reduce the load.
- Make sure some external force is not rotating the motor at start.
- Enable Speed Search Selection at start. (b3-01 = 1).