oH alarm code in yaskawa V1000 drive

1 Posts
1 Users
0 Reactions
284 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Heatsink Overheat comes when the temperature of the heatsink exceeded the overheat pre-alarm level set to L8-02 (90-100 °C). Default value for L8-02 is determined by drive model selection .

1. Surrounding temperature is too high.

• Check the surrounding temperature.
• Improve the air circulation within the enclosure panel.
• Install a fan or air conditioner to cool surrounding area.
• Remove anything near drive that may cause extra heat.

2. Internal cooling fan has stopped.

• Replace the cooling fan.
• After replacing the drive, set parameter o4-03 to 0 to reset the cooling fan operation time.

3. Airflow around the drive is restricted.

• Provide proper installation space around the drive as indicated in the manual.
• Allow for the proper space and ensure that there is sufficient circulation around the control panel.
• Check for dust or other foreign materials clogging the cooling fan.
• Clear debris caught in the fan that restricts air circulation.