Cause : Overtorque 1 comes when drive output current (or torque in OLV, CLV, AOLV/PM, and CLV/PM) was greater than L6-02 for longer than the time set to L6-03.
  1. Inappropriate parameter settings. Check parameters L6-02 and L6-03.
  2. There is a fault on the machine side (e.g., the machine is locked up).
    • Check the status of the machine.
    • Remove the cause of the fault.