Cause : Multi-Function Input Selection Error comes when a contradictory setting is assigned to multi-function contact inputs H1-01 to H1-07.
- The same function is assigned to two multi-function inputs or Excludes “Not used” and “External Fault.”
- Ensure all multi-function inputs are assigned to different functions.
- Re-enter the multi-function settings to ensure this does not occur.
- The Up command was set but the Down command was not, or vice versa (settings 10 vs. 11).
- Properly set the functions that required for use in combination with other functions.
- The Up 2 command was set but the Down 2 command was not, or vice versa.
- Properly set the functions that required for use in combination with other functions.(settings 75 vs. 76).
- Check if contradictory settings have simultaneously been assigned to the multi-function input terminals.