Cause : Initialization Required comes when the drive, control board, or terminal board have been replaced and the
parameter settings between the control board and the terminal board no longer match.
- Set A1-03 to 5550 to load the parameter settings stored in the terminal board to the drive.
- Initialize parameters after drive replacement by setting A1-03 to 2220 or 3330.