oPE07 alarm code in yaskawa U1000 drive

1 Posts
1 Users
0 Reactions
123 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Multi-Function Analog Input Selection Error comes when a contradictory setting is assigned to multi-function analog inputs H3-02, H3-10, or H3-06 and PID functions conflict.

  1. At least two analog input terminals are set to the same function (i.e., at least two of these parameters have the same setting: H3-02, H3-10, or H3-06).
  2. Change the settings to H3-02, H3-10, and H3-06 so that functions no longer conflict.
  3. The following simultaneous contradictory settings:
    • H3-02, H3-10, or H3-06 = B (PID Feedback) while H6-01 (Pulse Train Input) = 1 (PID Feedback)
    • H3-02, H3-10, or H3-06 = C (PID Target Value) while H6-01 = 2 (pulse train input sets the PID target value)
    • H3-02, H3-10, or H3-06 = C (PID Target Value) while b5-18 = 1 (enables b5-19 as the target PID value)
    • H6-01 = 2 (PID target) while b5-18 = 1 (enables b5-19 as the target PID value)
    Disable one of the PID selections.
 
 