oPE11 alarm code in yaskawa V1000 drive

1 Posts
1 Users
0 Reactions
279 Views
Posts: 18335
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Carrier Frequency Setting Error comes when the following simultaneous contradictory settings: C6-05 is greater than 6 and C6-04 is greater than C6-03 (carrier frequency lower limit is greater than the upper limit). If C6-05 is less than or equal to 6, the drive operates at C6-03.

  1. Upper and lower limits between C6-02 and C6-05 contradict each other.
  2. Correct the parameter settings.