Cause : Pulse Monitor Selection Error comes when incorrect setting of monitor selection for pulse train (H6-06). Scaling for the pulse train monitor is set to 0 (H6-07 = 0) while H6-06 is not set to 101, 102, 105, or 116.
- Change scaling for the pulse train monitor or set H6-06 to 101, 102, 105, or 116.