ov alarm code in yaskawa V1000 drive

1 Posts
1 Users
0 Reactions
491 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : DC Bus Overvoltage comes when the DC bus voltage exceeded the trip point. When a Yaskawa V1000 drive displays a "DC Bus Overvoltage" alarm, it indicates that the voltage level on the DC bus of the drive has exceeded the acceptable threshold. 

The DC bus voltage exceeded the trip point.
For 200 V class: approximately 410 V
For 400 V class: approximately 820 V (740 V when E1-01 < 400)

  1. Surge voltage present in the drive input power.
    • Install a DC link choke or an AC reactor.
    • Voltage surge can result from a thyristor convertor and a phase advancing capacitor operating on the same drive input power system.
  2. The motor is short-circuited.
  3. Check the motor power cable, relay terminals and motor terminal box for short circuits.
  4. Correct grounding shorts and turn the power back on.
  5. Ground current has overcharged the main circuit capacitors via the drive input power.