Cause : Undertorque Detection 1 comes when the current has fallen below the minimum value set for Torque Detection Level 1 (L6-02) for longer than the allowable time (L6-03).

  1. Parameter settings are not appropriate for the load.
  2. Check the settings of parameters L6-02 and L6-03.
  3. There is a fault on the machine side.
  4. Check the load for any problems.